Hi,
I'm developing on RevPi connect+ 32GB.
I want to use a relay at the connector X2 as a make relay like below.
Device power-off: relay Open
Device power-on: relay Close
However, the relay acts as below
Device power-off: relay Close
Device power-on: relay Close
I can open the relay via the status byte RevPiLED but I can't change the relay state when power off.
How can I change the relay settings?
Relay contact is closed when a device power is off
-
- Posts: 2
- Joined: 17 May 2022, 03:47
Re: Relay contact is closed when a device power is off
Hello,
unfortunately, it is not possible to keep the relay contact open when the Power is off: the revpi connect is equipped with a relay that is normally closed by default.
Best regards
Ulrich Kouatang Biakoup | Technical Support
unfortunately, it is not possible to keep the relay contact open when the Power is off: the revpi connect is equipped with a relay that is normally closed by default.
Best regards
Ulrich Kouatang Biakoup | Technical Support
- Attachments
-
- relay pic.PNG (260.48 KiB) Viewed 2986 times
-
- Posts: 2
- Joined: 17 May 2022, 03:47
Re: Relay contact is closed when a device power is off
Hello,
Thank you for your reply.
Can I choose Normal Open relay when I order Revpi?
Thank you for your reply.
Can I choose Normal Open relay when I order Revpi?
Re: Relay contact is closed when a device power is off
Hello,
No, it is not possible to choose normally open when ordering a Revpi. This is a stable convention.
How to use the relay see here: https://revolutionpi.com/tutorials/uebe ... rect=en_US
Best regard
Ulrich Kouatang Biakoup | Technical Support
No, it is not possible to choose normally open when ordering a Revpi. This is a stable convention.
How to use the relay see here: https://revolutionpi.com/tutorials/uebe ... rect=en_US
Best regard
Ulrich Kouatang Biakoup | Technical Support