Hi.
I am using the Modbus master with a physical connection to the RS-485 port on the RevPi Connect.
The Modbus-part is set up, and I read the values with piTest etc.
It seems to work fine, BUT - I saw that if the slave does not answer, the values in the process-image are kept.
How can I pick up on this ?
Alf
debugging ModBus
-
dirk
- Posts: 2271
- Joined: 15 Dec 2016, 12:19
Re: debugging ModBus
Hi Alf, you have to read and reset the status values, see here under "Help! Error!"
Modbus_Master_Status
Master_Status_Reset
Modbus_Action_Status_[1… 32]
Action_Status_Reset_[1… 32]
Modbus_Master_Status
Master_Status_Reset
Modbus_Action_Status_[1… 32]
Action_Status_Reset_[1… 32]
-
alf@emcom.no
- Posts: 20
- Joined: 25 Sep 2018, 08:17
Re: debugging ModBus
OK, so I can get the status, but when communication is restored, the read Modbus-values themselves will be updated again, right ?
-
dirk
- Posts: 2271
- Joined: 15 Dec 2016, 12:19
Re: debugging ModBus
Yes, if you have performed the reset of the Modbus communication accordingly then the values will be updated again.