RevPi Connect+ as Profinet device

05 Oct 2022, 10:56

Hello RevPi Community,

i have bought the Revpi Connect+ and the regarding license for Codesys for Raspberry Pi MC.
For my project the RevPi should interact as a Profinet client device to a superior Profinet master.
I have chosen the RevPi Connect because of the second RJ45-Port to use it simultaneously in an IT- and Profinet-Network.

My Problem is that i can not find a gsd-File for the Revpi Connect module only for the PN Gateway, so i can not bind the RevPi as Profinet device in codesys.

Is it possible at all to use the RevPi Connect as a PN Client without using a gateway or is the gateway necessary?

Thank you for your help!

Best Regards
mar_devSPS
 
User avatar
nicolaiB
KUNBUS
Posts: 773
Joined: 21 Jun 2018, 10:33
Answers: 1
Location: Berlin
Contact:

Re: RevPi Connect+ as Profinet device

05 Oct 2022, 11:55

Hi,

I'm not a CODESYS export, but maybe this tutorial can be helpful to you: http://soup01.com/en/2022/02/15/codesysusing-pi4-as-a-profinet-device/

-Nicolai
 
mar_devSPS
Topic Author
Posts: 3
Joined: 05 Oct 2022, 10:45
Answers: 0

Re: RevPi Connect+ as Profinet device

06 Oct 2022, 15:16

Sorry I am new to PN as well as Codesys and I still can not connect the RevPi to the Profinet master.
When I click on "scan for devices" on the PN_Controller in Codesys I am getting the error on the picture.
PN_1.PNG
PN_1.PNG (112.16 KiB) Viewed 5006 times
I think the problem is a missing GSD-file, that includes the ID number resp. Vendor-+Device-ID.

Is there any solution or am i doing something completely wrong?
Attachments
PN_2.PNG
PN_2.PNG (63.4 KiB) Viewed 5006 times
 
mar_devSPS
Topic Author
Posts: 3
Joined: 05 Oct 2022, 10:45
Answers: 0

Re: RevPi Connect+ as Profinet device

07 Oct 2022, 10:59

[SOLVED]
The Problem was a wrong firewall configuration (as stated in the error message) of the PN-Controller in the Soft-PLC from Codesys on Windows.
Not all programms from Codesys were allowed (especially CODESYSControlWinSysTray.exe), so the Soft PLC was blocked and could not get the PN connection to the RevPi.

Maybe this will help someone facing the same issues.
 
User avatar
nicolaiB
KUNBUS
Posts: 773
Joined: 21 Jun 2018, 10:33
Answers: 1
Location: Berlin
Contact:

Re: RevPi Connect+ as Profinet device

07 Oct 2022, 11:39

Thanks for letting us know your solution.

-Nicolai
 
panda78
Posts: 1
Joined: 03 Mar 2023, 07:44
Answers: 0

Re: RevPi Connect+ as Profinet device

03 Mar 2023, 07:48

I think this is a fantastic article, and I really appreciate you letting me know about it. That is precisely what I had hoped to find, and I really hope that you will keep sharing content that is of such high quality in the years to come.

Who is online

Users browsing this forum: No registered users and 0 guests