THANK YOU!
I have moved all modules to the right bridge and it works now.
It is definitely cleaner solution than mine. I made the config file read only...
Thank you again,
Tomas.
Search found 6 matches
- 08 Jul 2022, 20:03
- Forum: CODESYS
- Topic: Automatic overwriting of _config.rsc
- Replies: 5
- Views: 10675
- 30 Jun 2022, 11:12
- Forum: CODESYS
- Topic: Automatic overwriting of _config.rsc
- Replies: 5
- Views: 10675
Automatic overwriting of _config.rsc
Hello,
I am migrating my project to CODESYS and have an issue with "_config.rsc" file automatic generation.
1. If I create _config.rsc using Pictory (has about 5kB) everything works as it should, RevPi Core 3 and DIO module is active and operational.
2. If I create CODESYS project with only Core3 ...
I am migrating my project to CODESYS and have an issue with "_config.rsc" file automatic generation.
1. If I create _config.rsc using Pictory (has about 5kB) everything works as it should, RevPi Core 3 and DIO module is active and operational.
2. If I create CODESYS project with only Core3 ...
- 06 Jan 2020, 13:04
- Forum: PROCON-WEB IoT
- Topic: Problems when passing string and array variables from logiCAD
- Replies: 0
- Views: 30807
Problems when passing string and array variables from logiCAD
Hello,
I have two problems with passing variables from logiCAD to PROCON-WEB.
1. Strings
A string variable created in logiCAD is displayed in PROCON-WEB with quotation marks and the string is probably zero-based. For example the five-character string stored in five-character string variable ABCDE ...
I have two problems with passing variables from logiCAD to PROCON-WEB.
1. Strings
A string variable created in logiCAD is displayed in PROCON-WEB with quotation marks and the string is probably zero-based. For example the five-character string stored in five-character string variable ABCDE ...
- 25 Dec 2019, 11:58
- Forum: Hardware
- Topic: AIO module startup fault
- Replies: 6
- Views: 11536
Re: AIO module startup fault
I've had some time this week so i measured startup times of power supplies (MeanWell RPS-45-24 and MDR-40-24) i used. There is a difference of about 0.12s in the startup time and the voltage waveform is definitely different - see the attached image.
I hope it will help You to improve the AIO power ...
I hope it will help You to improve the AIO power ...
- 12 Dec 2019, 16:44
- Forum: Hardware
- Topic: AIO module startup fault
- Replies: 6
- Views: 11536
Re: AIO module startup fault
I have tested the MeanWell power supply MDR 40-24 and it looks the startup process works as it should.
The old power supply, which did not work, was made by the same manufacturer, but it was the medical safety version RPS 45-24. It has even 5W more power than the MDR version and in the catalogue it ...
The old power supply, which did not work, was made by the same manufacturer, but it was the medical safety version RPS 45-24. It has even 5W more power than the MDR version and in the catalogue it ...
- 06 Dec 2019, 11:00
- Forum: Hardware
- Topic: AIO module startup fault
- Replies: 6
- Views: 11536
AIO module startup fault
Hello,
I have RevPi Core3 with DIO and AIO modules.
During completion of our project, the problem with AIO module start-up appeared.
After power-on (after long period in the off state) the module stays in the phase when red power LED is blinking and is not detected by the Core unit.
Software reboot ...
I have RevPi Core3 with DIO and AIO modules.
During completion of our project, the problem with AIO module start-up appeared.
After power-on (after long period in the off state) the module stays in the phase when red power LED is blinking and is not detected by the Core unit.
Software reboot ...