Search found 3 matches
- 16 May 2019, 08:54
- Forum: logi.cals
- Topic: Analog input value in Logi.CAD3
- Replies: 5
- Views: 25749
Re: Analog input value in Logi.CAD3
Hello Johan,
thank you for the details.
After further internal clarification I can give you the following information:
The data type for the analog value is provided by "Pictory" to logi.CAD3. I think we would also need some informations from Kunbus how to get a higher solution for the analog ...
- 01 May 2019, 08:23
- Forum: logi.cals
- Topic: Analog input value in Logi.CAD3
- Replies: 5
- Views: 25749
Re: Analog input value in Logi.CAD3
Hello Johan,
Please tell us a little more about your (physically) application. What's the reason for the need of such a high resolution?
With current version of logi.CAD 3 it is not possible to get a higher resolution as WORD (16 bit).
kind regards
Walter
Hello Walter,
Thank you for your ...
- 30 Apr 2019, 13:41
- Forum: logi.cals
- Topic: Analog input value in Logi.CAD3
- Replies: 5
- Views: 25749
Analog input value in Logi.CAD3
Hallo,
I have a little problem that I can’t solve, I want to use the full 24 bit ADC of the AIO module in logi.CAD.
The 0 to 10 volts is displayed in a WORD value of 0 to 10.000 mV when I read the global input in Logi.CAD.
I want it to use the full 24 bit range of 0 to 16.777.216
Is it possible ...
I have a little problem that I can’t solve, I want to use the full 24 bit ADC of the AIO module in logi.CAD.
The 0 to 10 volts is displayed in a WORD value of 0 to 10.000 mV when I read the global input in Logi.CAD.
I want it to use the full 24 bit range of 0 to 16.777.216
Is it possible ...