MIO 1.2 input impedance change (900 kΩ → 20 kΩ) breaks readings from passive 0–10 V current transformers

Topics about the Hardware of Revolution Pi
petrjahoda
Posts: 4
Joined: 26 Nov 2024, 10:19

MIO 1.2 input impedance change (900 kΩ → 20 kΩ) breaks readings from passive 0–10 V current transformers

Post by petrjahoda »

Hello,

We have been using RevolutionPi with the MIO module for some time to read current via passive split-core current transformers (YHDC SCT010T-D, 10 A / 10 V variant, with built-in rectifier, output impedance ~7 kΩ).
With MIO version 1.1, everything worked correctly: a primary current of 10 A produced a reading of approximately 10000, and 5 A produced approximately 5000, using the standard 0–10 V input configuration in PiCtory. The high input impedance of MIO 1.1 (>900 kΩ) meant the CT was effectively unloaded and its output voltage matched its nominal rating.
After upgrading to MIO version 1.2, the same CTs on the same channels now produce significantly different (lower) values, and the relationship is no longer a simple linear scale of the old one. We traced this to the input impedance change from >900 kΩ in MIO 1.1 to 20 kΩ in MIO 1.2.

The problem is twofold:

The 7 kΩ output impedance of the CT now forms a significant voltage divider with the 20 kΩ MIO input (loaded output ≈ 74% of open-circuit value).
Because the CT contains an internal diode bridge rectifier and smoothing capacitor, the loading also introduces nonlinearity — diode forward drops and cap discharge between mains half-cycles cause additional, current-dependent droop. This means a single scaling factor cannot recover the original readings across the operating range.

Concrete example from our setup: at 3.04 A primary current (verified with a clamp meter), MIO 1.1 would have read approximately 3040. MIO 1.2 reads approximately 1995. Linear divider theory predicts ~2250, so we are seeing an additional ~250 mV of nonlinear droop on top of the divider effect.
We would prefer to solve this in software rather than adding op-amp buffer hardware to every installation, but multi-point per-channel calibration tables are impractical for us at scale, and they would not be temperature-stable due to the diode Vf drift in the CT's rectifier.
Our questions:

Is there any configuration option in MIO 1.2 (PiCtory or otherwise) to select a higher input impedance mode, similar to MIO 1.1?
Was the impedance change from >900 kΩ to 20 kΩ documented as a breaking change between MIO 1.1 and 1.2? We did not find it in the changelog.
Does KUNBUS have an official recommendation or application note for interfacing passive rectified current transformers (or similar high-source-impedance 0–10 V sensors) to MIO 1.2?
Are there other customers who have hit this issue after upgrading, and is there a recommended migration path that does not require adding external buffer circuitry to every deployed device?

Any guidance would be greatly appreciated. We have multiple deployed systems affected by this and would like to find a clean solution.

Thank you,
Petr Jahoda