Hello Wolfgang and PVCS,
Modbus RTU with Connect 4 on 64 bit image shall work with following settings :
Configure COM port default interface for Connect4 in /etc/CODESYSControl_User.cfg
running CODESYS Control for Linux ARM64 SL
[SysFile]
PlaceholderFilePath.1=/etc/revpi, $configrsc$
[SysCom ...
Search found 199 matches
- 25 Apr 2024, 14:07
- Forum: CODESYS
- Topic: RevPi RS485 config for use in CodeSys
- Replies: 10
- Views: 124172
- 24 Apr 2024, 09:46
- Forum: CODESYS
- Topic: Modbus RTU läuft nicht in Codesys - RevPI Connect 4
- Replies: 2
- Views: 37183
Re: Modbus RTU läuft nicht in Codesys - RevPI Connect 4
Hello Wolfgang,
Please follow the similar topic posted on the english forum.
viewtopic.php?t=4345
Viele Grüße, Amar
Please follow the similar topic posted on the english forum.
viewtopic.php?t=4345
Viele Grüße, Amar
- 23 Apr 2024, 17:32
- Forum: CODESYS
- Topic: RevPi RS485 config for use in CodeSys
- Replies: 10
- Views: 124172
Re: RevPi RS485 config for use in CodeSys
Hello PVCS,
Under General->Serial Port Configuration tab of MODBUS_COM device in codesys tree
COM Port selected will be as follows
/dev/ttyUSB0 -> COM Port 1
/dev/ttyUSB1 -> COM Port 2 ...
/dev/ttyUSBn -> COM Port n
In /etc/CODESYSControl_User.cfg you can try configuring following:
[SysCom ...
Under General->Serial Port Configuration tab of MODBUS_COM device in codesys tree
COM Port selected will be as follows
/dev/ttyUSB0 -> COM Port 1
/dev/ttyUSB1 -> COM Port 2 ...
/dev/ttyUSBn -> COM Port n
In /etc/CODESYSControl_User.cfg you can try configuring following:
[SysCom ...
- 27 Mar 2024, 09:50
- Forum: CODESYS
- Topic: Funny behaviour of inputs
- Replies: 3
- Views: 63926
Re: Funny behaviour of inputs
Hi,
Are you using 1.4.1.99 beta version of Revolution Pi Library for CODESYS?
For Connect 4 with RevPi Bullseye Image (64 bit) you need to use
CODESYS Control Linux ARM 64 bit.
There may be some incorrect device tree combination in your configured project.
I would recommend to first create a new ...
Are you using 1.4.1.99 beta version of Revolution Pi Library for CODESYS?
For Connect 4 with RevPi Bullseye Image (64 bit) you need to use
CODESYS Control Linux ARM 64 bit.
There may be some incorrect device tree combination in your configured project.
I would recommend to first create a new ...
- 26 Mar 2024, 11:14
- Forum: CODESYS
- Topic: CODESYS DIO Ausgänge und Eingänge 1..8 ok, 9..14 funktionieren nicht
- Replies: 1
- Views: 36842
Re: CODESYS DIO Ausgänge und Eingänge 1..8 ok, 9..14 funktionieren nicht
Hallo,
Möglicherweise liegt es an einem fehlerhaften Bitzugriff im konfigurierten Projekt.
Verwend die neueste Version der RevPi Codesys-Bibliothek.
Überprüf mal, ob das richtige DIO-Modul im Codesys-Gerätebaum konfiguriert ist.
(Verwendest du die Blinklicht-Demo, um einzelne Bits des ...
Möglicherweise liegt es an einem fehlerhaften Bitzugriff im konfigurierten Projekt.
Verwend die neueste Version der RevPi Codesys-Bibliothek.
Überprüf mal, ob das richtige DIO-Modul im Codesys-Gerätebaum konfiguriert ist.
(Verwendest du die Blinklicht-Demo, um einzelne Bits des ...
- 19 Feb 2024, 10:28
- Forum: Software
- Topic: piBridge with CODESYS Control for Raspberry PI 4.8.0.0 does not work
- Replies: 8
- Views: 48291
Re: piBridge with CODESYS Control for Raspberry PI 4.8.0.0 does not work
It is recommended to use latest Codesys control runtime.(CODESYS Control for Raspberry Pi MC V 4.10.0)
https://store.codesys.com/en/softplcs-for-applicationbased-licenses
Some other configuration (probably 1-Wire Busmaster) occupied the placeholder path on your configured device.
When you install ...
https://store.codesys.com/en/softplcs-for-applicationbased-licenses
Some other configuration (probably 1-Wire Busmaster) occupied the placeholder path on your configured device.
When you install ...
- 19 Feb 2024, 09:47
- Forum: Software
- Topic: Codesys with touch screen
- Replies: 10
- Views: 22642
Re: Codesys with touch screen
Hi Francois,
There is traditional touch panel based HMI soulution from CODESYS ecosystem
https://www.codesys.com/products/codesys-visualization/hmi.html
https://store.codesys.com/en/codesys-hmi-sl-bundle.html
More economical option is using a browser based HMI option usaing CODESYS WebVisu which ...
There is traditional touch panel based HMI soulution from CODESYS ecosystem
https://www.codesys.com/products/codesys-visualization/hmi.html
https://store.codesys.com/en/codesys-hmi-sl-bundle.html
More economical option is using a browser based HMI option usaing CODESYS WebVisu which ...
- 15 Feb 2024, 15:57
- Forum: Software
- Topic: RevPi Compact & Codesys
- Replies: 9
- Views: 16556
Re: RevPi Compact & Codesys
Analog Input channel should be configured to 0-10V in CODESYS Compact Parameters as in your test case.
Codesys Configuration overwrites pictory configuration.Pictory configuration is independent and not used together with codesys.
The combination with pictory and piTest was an alternate option ...
Codesys Configuration overwrites pictory configuration.Pictory configuration is independent and not used together with codesys.
The combination with pictory and piTest was an alternate option ...
- 15 Feb 2024, 14:55
- Forum: Software
- Topic: RevPi Compact & Codesys
- Replies: 9
- Views: 16556
Re: RevPi Compact & Codesys
Hi Vaggelis,
It works at my side as shown in screenshots below:
Compact Test.png
Compact Test 2.png
Test Project: CompactTestAI.zip
Attached project is tested with:
revolutionpibridge-V1.4.1.0
CODESYS Control for Raspberry PI 4.10.0.0
You can try other Analog inputs.
Test if Analog ...
It works at my side as shown in screenshots below:
Compact Test.png
Compact Test 2.png
Test Project: CompactTestAI.zip
Attached project is tested with:
revolutionpibridge-V1.4.1.0
CODESYS Control for Raspberry PI 4.10.0.0
You can try other Analog inputs.
Test if Analog ...
- 15 Feb 2024, 10:18
- Forum: Software
- Topic: RevPi Compact & Codesys
- Replies: 9
- Views: 16556
Re: RevPi Compact & Codesys
The previous picture shows wiring to Analog input CH 6.
Also, the input variable declared in CODESYS should be called in program in order to be updated cyclically.This can be done as shown in screenshots below.
Regards, Amar
Also, the input variable declared in CODESYS should be called in program in order to be updated cyclically.This can be done as shown in screenshots below.
Regards, Amar